In climates with low night-time temperatures, an energy-efficient way of cooling a house is to install a fan in the ceiling that draws air from the interior of the house and discharges it to a ventilated attic space. Consider a house whose interior air volume is \(\displaystyle 720 \ \text{m}^3\). If air in the house is to be exchanged once every \(\displaystyle 20\) minutes, determine \(\displaystyle \bold{(a)}\) the required flow rate of the fan and \(\displaystyle \bold{(b)}\) the average discharge speed of air if the fan diameter is \(\displaystyle 0.5 \ \text{m}\).
 
In climates with low night-time temperatures, an energy-efficient way of cooling a house is to install a fan in the ceiling that draws air from the interior of the house and discharges it to a ventilated attic space. Consider a house whose interior air volume is \(\displaystyle 720 \ \text{m}^3\). If air in the house is to be exchanged once every \(\displaystyle 20\) minutes, determine \(\displaystyle \bold{(a)}\) the required flow rate of the fan and \(\displaystyle \bold{(b)}\) the average discharge speed of air if the fan diameter is \(\displaystyle 0.5 \ \text{m}\).
Please show us what you have tried and exactly where you are stuck.

Please follow the rules of posting in this forum, as enunciated at:


Please share your work/thoughts about this problem
 
determine \(\displaystyle \bold{(b)}\) the average discharge speed of air if the fan diameter is \(\displaystyle 0.5 \ \text{m}\).
\(\displaystyle \bold{average \ discharge \ speed} = \frac{\bold{flow rate}}{A} = \frac{0.6}{\pi\left(\frac{0.5}{2}\right)^2} = \textcolor{blue}{3.056 \ \text{m/s}}\)
 